The State of Illinois Plumbing Code does not specifically address water powered sump pumps. An Illinois-based battery backup sump pump manufacturer advertises heavily that an RPZ is required, as they want the customer to buy their product verses a water powered pump. The Backflow Committee has also discussed this topic on numerous occasions.
The stance of the IDPH is that ground water is not a high hazard and a vented dual check valve is acceptable backflow protection for a water powered sump pump. Note however that being the water purveyor, you can still require an RP at the pump or at the water meter. State standards are a minimum and you have a right to enforce stricter regulations as long as you have it written in an ordinance, policy manual, or similar.