I only have one question. What type of backflow device need to be installed on a beauty salon that use hair chemicals???????????????????????



Laurie Dougherty - Illinois Section AWWA
laurie@isawwa.org
cell or text 815-970-2145


11/5/2013 at 10:02:26 PM GMT
Posts: 602
Along with the backflow protection at the point-of-use as required by Plumbing Code, the site is considered a high hazard and an RP should be installed at the meter to protect your distribution system