RPZ Backflow Devic
Is a RPZ Backflow Device ok to use in a underground pit if a floor drain is installed to remove any ground waterseepage into pit or discharge from RPZ

Laurie Dougherty - Illinois Section AWWA
laurie@isawwa.org
cell or text 815-970-2145


11/5/2013 at 10:44:51 PM GMT
Posts: 602
Illinois does not allow for any type of backflow preventer to be placed underground or in a pit. Even if the pit has a sump pit/pump, floor drain, etc.

Section 890.1130 Protection of Potable Water

g) Installation of Devices or Assemblies.

5) Double Check Valve, and Reduced Pressure Principle Backflow Preventer Assemblies. No in-line double check valve backflow preventer assembly (DCV) or reduced pressure principle backflow preventer assembly (RPZ) shall be located more than 5 feet above a floor, or be installed where it is subject to freezing or flooding conditions.